alpa_sheth ...
Posted: Mon Nov 19, 2012 3:22 amPost subject: Welcome to the Econference on Design and Construction of Tal |
Dear All:�
Greetings and welcome to the E-conference on Design and Construction of Tall Buildings in India. As has been mentioned earlier the conference will run Nov. 19 through Nov 28.�
A few pointers on Econference protocol.�
* All topics pertaining to Tall Buildings may be discussed and we will �urge all of you to participate in adding value to a topic with informed and well-thought out comments so as to maintain the �standard of the Econference to international quality. We request that you please keep your subject note or comment on an issue crisp and �topical.�
* Any issues which are not core to the technical part of the Econference may please be discussed on the SpeakOut forum, not in the Econference, please.�
* Kindly limit �discussions to � max of two issues pertaining to tall buildings �in a single mail. The issues should be in different paragraphs. Also, when differing with another commentator, pl exercise utmost civility while expressing �your disagreement.�
We had suggested some topics for discussion and we had received valuable input from all of you. We have incorporated your suggestions and produced a revised list as under. This is not an exhaustive list and other pertinent technical issues can be added as required.�
我们有一个系统t of subject experts for the Econference. We will introduce them along the way. We look forward to some exciting days ahead.....�
warm regards,
Alpa Sheth� Prof CVR Murry Prof Swaminathan Krishnan�
Econference Moderators�
Topics for Tall Buildings Conference �� What do we define as a tall building?
一)�����高层建筑的选址:�� � � � i Where are tall buildings allowed/not allowed to be sited? b)����� Geotechnical� Issues�
- � Soil Testing for Tall Buildings.�
- � Testing for establishing soil and pile modulus�
c)����� General Parameters of Tall Buildings�
- �Geometric Proportioning�
- �Height and Aspect Ratio�
- �General Distribution and area of� Vertical� and Lateral load carrying elements as % of plan area for concrete and steel structures.�
- Min required stiffness of building�
- Perimeter offset to avoid pounding�
d)������ Structural Configuration, Structural Systems and their Behaviour�
- � Selection of Structural system- Preliminary behavior analysis � of alternative systems�
- Discussion of Strucutral Sustems- Frames, Shear Walls, Frame-Shear Walls, Slab-Column Shear Wall structure, Tube Stucture, Hybrid Structure.....
- � Performance of different structural systems;�
- � What levels of ductility are achievable in the lateral force resisting systems being constructed in India?� What should the value of R be?�
- Hybrid Structural Systems and their behaviour�
- �Achieving �redundancy and alternative load path�
d)����� Load Combinations�
e)������ Use of Masonry partition walls in tall buildings
- �Should they be included in �analysis?�
- �Should they be isolated from structure or not?�
- �任何特殊规格分区的墙壁�tall buildings? �(Light weight etc.)�
f)����� Modeling and Analysis
- Appropriate Modelling tools and soft ware for elastic, inelastic design for different systems and elements�
� g)����� Structural Irregularities
- Should structural system transfer be allowed in tall buildings? If yes what are the limitations to be observed?�
- Soft storey, Weak Storey�
- How to deal with torsional irregularity? How much max� modal mass may be excited in torsional modes of vibration?�
h)������� Wind Design
- �When should Wind Tunnel Testing be carried out?�
- What are the wind tunnel �tests that should be carried out and to what effect?� How to account for future buildings in the neighborhood in the layout and configurtion of adjacent buildings in the wind tunnel?�
- What are the results to be asked from the WT testing agency?�
- Appropriate Damping Values�
- Discussion on Wind Dampers- When to use them, What type to use for what building application?�
- Should there be instrumentation on tall buildings for measurement of vibrations/accelerations?�
� i)������� Earthquake Analysis and Design
- Does the current IS 1893 assure acceptable performance of tall buildings?�
- Seismic hazard characterization (base shear, response spectrum, ground motion histories, near-source effects, fault maps, fault classification w.r.t. earthquake potential characterization).�
- Site soil characterization.�
- Closely spaced modes-How critical is this issue? ��
- � Linear static analysis procedure.�
- �Dynamic response spectrum procedure.� What should the spectrum look like?� When should a site-specific spectrum be required?� How to account for near-source effects (applies to linear static procedure as well)?�
- When should one do non-linear analysis? What are the earthquake ground motions to be considered in Indian scenario? �
- �How to properly account for P-Delta effects (modeling gravity columns)?� Do we have software for nonlinear analysis readily available?� Are test data� characterizing component nonlinear (cyclic) behavior using prevailing Indian standards of practice available?� What should the material models look like for various structural components?�
- �When is a pushover analysis required?�
���������� j) � ��� �Frame Structure -Ductile detailing criteria: �
- ��� What criteria and when applicable? �
- ��� Strong-column weak beam in moment frames�
- ��� �boundary elements in shear walls�
- ��� �tie-spacing�
- ��� �135 degree hooks�
- ��� �lap-splices and development length�
- ��� �location of splices�
- ��� �beam-column joint detailing in concrete frames�
- ��� �continuity of column vertical rebar and beam longitudinal rebar through the joint�
- ��� �link beam detailing (diagonal rebar)�
- ��� �required level of diaphragm attachment on either side of a given length of wall, etc.�
- ��� When and where is Capacity Design required?�
- � Column (gravity/lateral) design (include long-term axial shortening of columns due to creep and its effects on beams/floor slabs, etc.);�
- �Use of composite sections for creep control.�
k) Shear Wall�
- Wall design (include long-term axial shortening due to creep)�
- ��Link beam design�
- �Diaphragm design�
l)�Energy dissipation devices
- viscous fluid dampers
- added stiffness and damping devices
m) � � � Use of Precast in Tall Building Construction�
- Should it be permitted?�
- To be used for which� elements of structure?�
- Design and detailing of joints?�
- Behaviour in past earthquakes�
n)������� Foundations a.������ Discussion on Piled raft foundations ��� Allowable deformations ��� Pile-raft interaction 对桩筏����分析 . � Shoring for Deep Basements �� ��� Pile testing for deep piles� ��� Max allowable deformation of piles of piled raft- codal provisions? ��� Deformations in piled raft? ��� Differential settlement between core and perimeter.� Provide a pour strip to minimize such settlement (when to provide).� Additional moments in beams and slab due to such differential settlement. ��� Design methodology and detailing of piles and rafts; lateral shear capacity of piles, vertical load carrying capacity of piles (skin friction vs bearing). b.����� Raft� foundations for tall buildings c.������ Pile foundations for Tall buildings�
� o)��� Facades
- Stiffness�
- Isolation;� Designing the fa�ade system to permit movement corresponding to wind and seismic drift limits.�
p)����� Tall Building with Podium issues
- Should tower be connected to Podium?� When?�
- Should Basement walls be considered in Analysis?�
- �Any special considerations to cater for large shear transfer in the podium diaphragm from tower? (refer ATC)�
q)����� Performance Criteria
- Serviceability Requirements�
- What should be the limiting acceleration values for human comfort level in wind design?�
- What is max drift to be allowed in wind and earthquake?� What can be the sudden spike in interstorey drift due to a soft/weak storey?�
r)����� Performance Based (Seismic) Design of Structures
- When to do this?�
- How to do it?�
- Review Procedures ....�
s)����� Other Detailing Aspects of Tall Buildings
- �Detailing of cold joints (Core and floor slab done separately)�
- Dealing with congestion of steel�
- Splices/Anchorages�
- Expansion Joint issues�
- Seismic joints:� When to use and how to design.�
- Design of Inclines Columns, Bracings etc.
t)������ Construction Issues of Tall Buildings
- Modular/Lightweight shuttering�
- Slipform Shuttering�
- High strength concretes � Issues of microcracking, delayed strength, additives, flyash, silica fumes etc.�
- High Grade Steel- Inconsistency in yield stress. �
- Dealing with congestion of steel �in beam-column joints�
- Vertical Transportation of concrete�
- Durability of Tall Buildings- How to repair/retrofit?�
- Concrete grade of columns vs. concrete grade of slabs � How to deal with difference?�
u)������ Construction Specifications
- Materials (including welds, rebar, concrete, structural steel, etc.)�
- Structural, Mechanical, Electrical, Plumbing, Vertical Transportation systems�
- Site preparation and managementa
v) � � � �Green Building Issues�
Posted via Email |
Back to top |
Econf_Moderator E-Conference Moderator
Posted: Mon Nov 19, 2012 3:26 amPost subject: Welcome to the Econference on Design and Construction of Tal |
Dear All:�
warm regards,
- ��� �tie-spacing�
k) Shear Wall�
� o)��� Facades
- Stiffness�
- When to do this?�
- How to do it?�
Posted via Email |
Back to top |
napeera SEFI Member
Posted: Mon Nov 19, 2012 4:15 amPost subject: Welcome to the Econference on Design and Construction of Tal |
Dear all,It is my privilege to be a member of this very highly professional and knowledgeable forum from which I have benefited a lot. 5 stars from me for starting this very informative E-Conference, which will help immensely, the structural engineers who must have just started designing tall structures.My first question will be. What is the definition of Tall Building in detail?Regards & best of luck. NAPeera - from Vodafone From:"alpa_sheth" Date:Mon, 19 Nov 2012 09:00:03 +0530 To: ReplyTo:econf34289@www.bussiapp.com Subject:[E-CONF] Welcome to the Econference on Design and Construction of Tall bUildings
亲爱的所有:�E-conferen问候和欢迎ce on Design and Construction of Tall Buildings in India. As has been mentioned earlier the conference will run Nov. 19 through Nov 28.� A few pointers on Econference protocol.� * All topics pertaining to Tall Buildings may be discussed and we will �urge all of you to participate in adding value to a topic with informed and well-thought out comments so as to maintain the �standard of the Econference to international quality. We request that you please keep your subject note or comment on an issue crisp and �topical.� * Any issues which are not core to the technical part of the Econference may please be discussed on the SpeakOut forum, not in the Econference, please.� * Kindly limit �discussions to � max of two issues pertaining to tall buildings �in a single mail. The issues should be in different paragraphs. Also, when differing with another commentator, pl exercise utmost civility while expressing �your disagreement.� We had suggested some topics for discussion and we had received valuable input from all of you. We have incorporated your suggestions and produced a revised list as under. This is not an exhaustive list and other pertinent technical issues can be added as required.� We have a list of subject experts for the Econference. We will introduce them along the way. We look forward to some exciting days ahead.....� warm regards, Alpa Sheth� Prof CVR Murry Prof Swaminathan Krishnan� Econference Moderators� ********************* Topics for Tall Buildings Conference �� What do we define as a tall building? a)����� Siting of tall buildings:�� � � � i Where are tall buildings allowed/not allowed to be sited? b)����� Geotechnical� Issues�
d)����� Load Combinations� e)������ Use of Masonry partition walls in tall buildings
- ��� �tie-spacing�
k) Shear Wall�
n)������� Foundations a.������ Discussion on Piled raft foundations ��� Allowable deformations ��� Pile-raft interaction ��� Analysis of piled rafts� . � Shoring for Deep Basements �� ��� Pile testing for deep piles� ��� Max allowable deformation of piles of piled raft- codal provisions? ��� Deformations in piled raft? ��� Differential settlement between core and perimeter.� Provide a pour strip to minimize such settlement (when to provide).� Additional moments in beams and slab due to such differential settlement. ��� Design methodology and detailing of piles and rafts; lateral shear capacity of piles, vertical load carrying capacity of piles (skin friction vs bearing). b.����� Raft� foundations for tall buildings c.������ Pile foundations for Tall buildings� � o)��� Facades
- Stiffness�
- When to do this?�
- How to do it?�
v) � � � �Green Building Issues� --
Posted via Email |
Back to top |
dssri SEFI Member
Posted: Mon Nov 19, 2012 5:50 amPost subject: Welcome to the Econference on Design and Construction of Tal |
1. How do we define a tall building - absolute height, aspect ratio, method of construction or the sesimic zone it is situated 2.着手一幢高楼——一个ny regulation needed to restrict the construction of tall buildings only to builder/developer/contractor having prior experience
god bless D S SRIDHAR ME, FIE, FIV, AMP (IIM) G 908 Mantri Tranquil Sy. No. 7/9/13 Gubalala Kanakapura Road BANGALORE 560061 KARNATAKA INDIA CELL +91-9845094486 dssri64@gmail.com (dssri64@gmail.com) sridhar.ds@alumni.iimb.ernet.in (sridhar.ds@alumni.iimb.ernet.in)
Quote: |
-- Original Message -- From:Econf_Moderator (forum@www.bussiapp.com) To:econf34289@www.bussiapp.com(econf34289@www.bussiapp.com) Sent:Monday, November 19, 2012 11:00 AM Subject:[E-CONF] Re: Welcome to the Econference on Design and Construction of Tal
Dear All:
* All topics pertaining to Tall Buildings may be discussed and we will urge all of you to participate in adding value to a topic with informed and well-thought out comments so as to maintain the standard of the Econference to international quality. We request that you please keep your subject note or comment on an issue crisp and topical.
* Kindly limit discussions to max of two issues pertaining to tall buildings in a single mail. The issues should be in different paragraphs. Also, when differing with another commentator, pl exercise utmost civility while expressing your disagreement.
warm regards,
Alpa Sheth Prof CVR Murry Prof Swaminathan Krishnan
a) Siting of tall buildings: i Where are tall buildings allowed/not allowed to be sited? b) Geotechnical Issues
- 土壤测试for Tall Buildings.
- Testing for establishing soil and pile modulus
c) General Parameters of Tall Buildings
- Geometric Proportioning
- Height and Aspect Ratio
- General Distribution and area of Vertical and Lateral load carrying elements as % of plan area for concrete and steel structures.
d) Structural Configuration, Structural Systems and their Behaviour
- Selection of Structural system- Preliminary behavior analysis of alternative systems
- Performance of different structural systems;
- What levels of ductility are achievable in the lateral force resisting systems being constructed in India? What should the value of R be?
- Achieving redundancy and alternative load path
d) Load Combinations
e) Use of Masonry partition walls in tall buildings
- Should they be included in analysis?
- Should they be isolated from structure or not?
- Any special specifications for partition walls of tall buildings? (Light weight etc.)
f) Modeling and Analysis
g) Structural Irregularities
- How to deal with torsional irregularity? How much max modal mass may be excited in torsional modes of vibration?
h) Wind Design
- When should Wind Tunnel Testing be carried out?
- What are the wind tunnel tests that should be carried out and to what effect? How to account for future buildings in the neighborhood in the layout and configurtion of adjacent buildings in the wind tunnel?
我)地震Analysis and Design
- Linear static analysis procedure.
- Dynamic response spectrum procedure. What should the spectrum look like? When should a site-specific spectrum be required? How to account for near-source effects (applies to linear static procedure as well)?
- How to properly account for P-Delta effects (modeling gravity columns)? Do we have software for nonlinear analysis readily available? Are test data characterizing component nonlinear (cyclic) behavior using prevailing Indian standards of practice available? What should the material models look like for various structural components?
- When is a pushover analysis required?
j) Frame Structure -Ductile detailing criteria:
- � What criteria and when applicable?
- � Strong-column weak beam in moment frames
- � boundary elements in shear walls
- � tie-spacing
- � 135 degree hooks
- �lap-splices长度和发展
- � location of splices
- � beam-column joint detailing in concrete frames
- � continuity of column vertical rebar and beam longitudinal rebar through the joint
- � link beam detailing (diagonal rebar)
- � required level of diaphragm attachment on either side of a given length of wall, etc.
- � When and where is Capacity Design required?
- Column (gravity/lateral) design (include long-term axial shortening of columns due to creep and its effects on beams/floor slabs, etc.);
- Use of composite sections for creep control.
k) Shear Wall
- Link beam design
- Diaphragm design
l) Energy dissipation devices
m) Use of Precast in Tall Building Construction
- To be used for which elements of structure?
n) Foundations a. Discussion on Piled raft foundations � Allowable deformations � Pile-raft interaction � Analysis of piled rafts . Shoring for Deep Basements � Pile testing for deep piles � Max allowable deformation of piles of piled raft- codal provisions? � Deformations in piled raft? � Differential settlement between core and perimeter. Provide a pour strip to minimize such settlement (when to provide). Additional moments in beams and slab due to such differential settlement. � Design methodology and detailing of piles and rafts; lateral shear capacity of piles, vertical load carrying capacity of piles (skin friction vs bearing). b. Raft foundations for tall buildings 桩基础Tall buildings
o) Facades
- Stiffness
- Isolation; Designing the fa�ade system to permit movement corresponding to wind and seismic drift limits.
p) Tall Building with Podium issues
- Should tower be connected to Podium? When?
- Any special considerations to cater for large shear transfer in the podium diaphragm from tower? (refer ATC)
q) Performance Criteria
- What is max drift to be allowed in wind and earthquake? What can be the sudden spike in interstorey drift due to a soft/weak storey?
r) Performance Based (Seismic) Design of Structures
- When to do this?
- How to do it?
s) Other Detailing Aspects of Tall Buildings
- Detailing of cold joints (Core and floor slab done separately)
- Seismic joints: When to use and how to design.
t) Construction Issues of Tall Buildings
- Dealing with congestion of steel in beam-column joints
u) Construction Specifications
v) Green Building Issues
Posted via Email |
Back to top |
Engineer SEFI Member
Posted: Mon Nov 19, 2012 6:06 amPost subject: Econference on Design and Construction of Tall Blgds - Seism |
I have attached herewith draft document prepared by CTBHU Committee on Seismic Design of Tall Buildingswww.ctbhu.org
Regards, Hemant Gor
Posted via Email
Warning:
Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners
here
and
here
to upload downloaded attachment to check for safety.
Description: |
Download |
Filename: |
CTBHU_Guide_Sesimic_Design_of_Tall_bldgs.pdf |
Filesize: |
1.99 MB |
Downloaded: |
1134 Time(s) |
Back to top |
prasadam_iitm SEFI Member
Posted: Mon Nov 19, 2012 6:33 amPost subject: Welcome to the Econference on Design and Construction of Tal |
On 19-Nov-2012, at 11:00 AM, Econf_Moderator wrote:
Quote: |
Dear All:
warm regards,
h) Wind Design
- � tie-spacing
- �lap-splices长度和发展
k) Shear Wall
- Link beam design
- Diaphragm design
o) Facades
- Stiffness
- When to do this?
- How to do it?
Meher Prasad Anumolu Professor, Department of Civil Engineering IIT Madras prasadam@iitm.ac.in (prasadam@iitm.ac.in)
Posted via Email |
Back to top |
drferozkottamal SEFI Member
Posted: Mon Nov 19, 2012 8:52 amPost subject: Welcome to the Econference on Design and Construction of Tal |
How to check safety against overturning, what should be the height aspect ratio, geometric proportioning...
On 19 November 2012 06:30, alpa_sheth forum@www.bussiapp.com)> wrote:
Quote: |
Dear All:�
warm regards,
- ��� �tie-spacing�
k) Shear Wall�
� o)��� Facades
- Stiffness�
- When to do this?�
- How to do it?�
Posted via Email |
Back to top |
ishacon Silver Sponsor
Posted: Mon Nov 19, 2012 10:15 amPost subject: Welcome to the Econference on Design and Construction of Tal |
Dear All,
It is indeed very heartening to see that this Econf has kicked off with Welcome Notes from eminent engineers and Professors. Permit me to voice some of my concerns in general.
Having been involved in Design audits of several tall buildings ( 75 meter height and above), in NCR region during last more than a decade, I have seen at close quarters the dire need of improvement in preparation of the drawings and careful checking thereof. Shortage of trained manpower for checking and the copy, paste routines of CAD by the draftsmen leave many errors untraced. This practice needs to be stopped at the consultant's end.
Due to the urgencies imposed by the Builder / developer, often the Structural Consultant is compelled to perform the analysis based on half baked inputs from the Architect and he has to issue foundation drawings with column schedules without having gone through detailed investigations on analysis front since the excavation is already done. Often the soil investigation reports do not do full justice to the testing and making appropriate recommnedations. It is about time, that everyone in the industry recognise the perils of doing so.
V.P. Agarwal B.Tech (IITMadras), M.Engg (USA)
ISHA CONSULTANTS (P) LTD NEW DELHI 110074
PH : 011-2630 1158 ; 08010071749 ; 093 1345 2180
Quote: |
-- Original Message -- From:prasadam_iitm (forum@www.bussiapp.com) To:econf34289@www.bussiapp.com(econf34289@www.bussiapp.com) Sent:Monday, November 19, 2012 3:00 PM Subject:[E-CONF] Re: Welcome to the Econference on Design and Construction of Tal
On 19-Nov-2012, at 11:00 AM, Econf_Moderator wrote: :Dear All:
warm regards,
h) Wind Design
- � tie-spacing
- �lap-splices长度和发展
k) Shear Wall
- Link beam design
- Diaphragm design
o) Facades
- Stiffness
- When to do this?
- How to do it?
Meher Prasad Anumolu Professor, Department of Civil Engineering IIT Madras prasadam@iitm.ac.in (prasadam@iitm.ac.in) (prasadam@iitm.ac.in (prasadam@iitm.ac.in))
Posted via Email |
Back to top |
BJREDDY SEFI Member
Posted: Mon Nov 19, 2012 11:20 amPost subject: |
Dear All
My best wishes to SEFI organizers for creating this excellent platform for sharing knowledge about tall buildings. I am much excited and enthusiastic to participate in this E-conference. I would like to share this document prepared by CTBUH, which will basically explain "Criteria for the Defining and Measuring of Tall Buildings".
Thanks & Regards, BJReddy
Warning:
here
and
here
Description: |
Criteria for the Defining and Measuring of Tall Buildings |
Download |
Filename: |
CTBUH_Height Criteria.pdf |
Filesize: |
843.43 KB |
Downloaded: |
1897 Time(s) |
Back to top |
partha at adaptsoft.com Guest
Posted: Mon Nov 19, 2012 11:21 amPost subject: Welcome to the Econference on Design and Construction of Tal |
Thank you for starting such an informative session. While I go through the topic I have following comments:
1. What should be ideal classification of Tall Building?
2.About Material, let us talk more Steel and Post Tension Concrete. As use of Reinforced Concrete will reduce the head room (for the presence of beam and thicker slab) and increase the building weight thus experience higher magnitude of Seismic Force.
3. Can we have a single document (according to the topics) containing details at the end of the conference?
Regards,
Partha Pratim Roy Vice President (Technical) ADAPT Concrete Software www.adaptsoft.com
From:Econf_Moderator (forum@www.bussiapp.com) Sent:Monday, November 19, 2012 11:00 AM To:econf34289@www.bussiapp.com(econf34289@www.bussiapp.com) Subject:[E-CONF] Re: Welcome to the Econference on Design and Construction of Tal
Dear All:
warm regards,
h) Wind Design
- � tie-spacing
- �lap-splices长度和发展
k) Shear Wall
- Link beam design
- Diaphragm design
o) Facades
- Stiffness
- When to do this?
- How to do it?
Posted via Email |